NEC Article 210-21(b)(3) quite clearly states that a 15 amp receptacle can be put on a 20 amp circuit. It would not be a big mistake and is quite common.
Unless of course it is the only recptacle on the circuit. Then you have to size them the same. Article 210-21(B)(1)
And then there is Article 210-21(b)(2) dealing with the total cord-and-plug-connected load. Which states that it should not exceed 80% of the receptacle rating. So if you really want to be sure of what you need, sit down and figure out everything in your house tonight that is cord-and-plug connected and figure out exactly what amps it is drawing and if you go over that 80% then you should find a new receptacle to plug stuff into. I know of absolutely no average person that lives in a house and computes their total load and rearranges accordingly. 99.9% of people just plug it in and expect it to work. The average aquarium in a persons home does not draw 12 amps (80% of 15). That's an average person's tank not a 10000 gallon tank with 10-250 watt halides, 10 vho's and pumps up the ---.