Originally Posted by
SCSInet
http:///forum/post/2727631
Oversubscribing panels is a very common and accepted practice. If I'm not mistaken the NEC does stipulate limits as to how much they can be oversubscribed.
However, in your case, I don't think you are oversubscribed.
You have a 200A main breaker. Homes are fed by two hot legs, each feeding a groupf of 120v breakers, and in some cases, both legs feeding the 240v circuits. That means the breaker will allow 200A on each of the two legs coming in simultaneously.
If you simply added up the amperages of all your breakers, and found 375A, you are actually undersubscribed. 200A * 2 legs = 400amps at 120v. With the exception of the few double pole breakers, the breakers in your box only use one of the two legs, and the two legs are to some extent evenly divided. Most panels have two vertical rows of breakers. It would go something like this for legs A and B.
A A
B B
A A
B B
A A
....
Granted, one leg will probably have a few more 15A breakers versus 20A breakers hanging off of it, so the loading of each leg would not be 100% even, but it would be somewhat close. If you were to apply the above diagram to your breakers and add up all the (A) and all the (B) separately, you'd probably find that they are somewhat close.
So seriously... adding a 20A circuit or two will not cause an issue. If you had access to a clamp-ammeter so you could check the actual amount of current flowing in those two main wires, you'd probably be surprised just how little you have in most conditions. My home commonly pulls about 30-40A on each leg when the AC is running and we have TVs on, lights, and my tank's lights are on.
I run three AC units, an electric dryer, my 180g reef (halides, chiller, the works), and a wood shop with several large machines all on a 150a service and I am nowhere near my limit.
...oh and one last point... if you are adding the tank to the house, you are adding the electrical load whether you add circuits or not. It makes no difference if you have 20 circuits or 100 circuits on your service, the total draw is what matters, so if you are adding that tank, you are putting the load in place whether or not you add breakers for it.