Also on my circuits it says: 10kA 120/240v
Does that mean my circuit is 10amps? Anyway to upgrade to a 20amp or would I have to get another breaker box?
 

turningtim

Active Member
First! if you have question about your box or breakers or maybe even service I would call an electrician to take a look.IF you are inclined it is something you CAN do yourself BUT you're messing with a bit of power in a CB box!
Your amp rating for individual breakers should be right on the lever of the breaker itself. It should say 15amp or 20amp for single pole and 30+ for double pole.
To up grade a 15a to a 20a you need to make sure the wire that you have will carry a 20a circuit. 15 amp = 14 gauge wire and 20 amp =12 gauge wire. DO not place a 20amp breaker on a 14 gauge wire. Especially with the amount of load we put on a circuit for our tanks!
I will be happy to help BUT
if you are not sure call a PRO
!
HTH
Tim
 