Originally Posted by
salty blues
http:///forum/post/3019666
IMO a GFCI alone is all that is really needed. It will most certainly trip under a fault condition whether a probe is used or not because of the nature that a GFCI operates, which is to sense any sudden current imbalance between the "hot" and the "neutral" conductors in the circuit. This is why GFCI's will work even on older wiring that has no "ground" in the circuit.
That being said, having a probe in conjunction with a GFCI certainly won't hurt, but every system should certainly have at least a GFCI.
You're partially correct.
It's true that a GFI will work on an ungrounded system because in a fault condition, the current is finding an alternate path to ground, usually through the user of the equipment to a non electrical ground, such as bare earth, a water pipe, etc.
In the case of a GFI on a fish tank, if the water is not tied to ground, when a fault occurs, the water will sit, electrically live. However, because there is no ground path anywhere (throught the GFI or otherwise), the GFI will not trip. No current will flow because it's an incomplete circuit. When a user who is grounded elsewhere sticks his hand in the water, the circuit is complete, current flows, the user receives a shock, and the GFI will trip.... in that order.
Of course, the GFI is designed to trip before dangerous amounts of current can pass, but still... I'd rather not recieve the shock in the first place.
Now, many hobbyists will argue that this is actually a more ideal situation, becuase that way the GFI will trip when the hobbyist is right there at the tank, rather than tripping in the middle of the night or when nobody is home to power the tank back up. I suppose that's a valid point.
In the end, I guess it all comes down to what school of thought you want to subscribe to.
But at any rate, the difference in current between hot and neutral that a GFI identifies and trips over cannot occur until the current has an alternate path to ground. If the water is not grounded, no alternate path (and hence no trip) can occur until the water is grounded... which would likely be through a human...
What I always tell people is no GFI, no probe... NOT SAFE. Probe, no GFI... NOT SAFE. GFI and no probe... SAFE. GFI and probe... SAFE.