The lights aren't the problem.
The lights have a grounded reflector. The water has become energized from a piece of failed equipment in the water. When you touch the water and the grounded reflector, the current finds a path through you to the grounded reflector, causing a shock. This is called a Ground Fault, and it is exactly the type of situation a GFI is designed to protect.
Don't bother trying to test with meters, it won't give anything resembling accurate measurements for a number of technical reasons I won't bore you with. First step, get a GFI on your tanks' equipment. Second step, place a grounding probe in the tank. The GFI should trip the moment a connected grounding probe is dunked into the water. Unplug all equipment from the GFI, reset it, leave the probe in the water, then plug one thing in at a time until you find the one that trips it. That's the quickest, easiest way to find the problem, and you'll have a safe, well protected tank when you are done!
An analog type meter MIGHT be more accurate, or any kind of meter wich actually requires a load to function....at the voltage that is present that is, prossibly anywhere from 25 to 130v. Who knows exactly whats present though until you test it.
Digitals are really no good for this.
In all likelihood, it will be a submersible piece of equipment. My recommendation is to discard whatever it is, do not try to repair a faulty submersible piece of equipment. Once the factory seal goes, there is no safe way to repair it yourself.
I have succesfully and easy repaired a heater before that lost the seal through the top of the test tube. Not a big deal really, just a rubber stopper inserted into a tube. But I wasnt recomending this necessarily. Pumps, IMO, once the seal has been broken and the windings are exposed to SW will not live much longer anyways. Cords can be properly repaired. Bonds can be remade.